wire comunication hmi E100 to pc for upload or receive
hi, i need help for comunication whit hmi e100 to mitshubushi.
Is the wired communication rs232-rs232 or rs422 -rs232? and how is the configuration in the connection.
Hi,
RS232 use for Programming. And RS422 for Mitsubishi PLC communication.
You can use SC-09 Red Cable directly for HMI to PLC communication.
Good Luck
Thanks.
Hello, thanks for the answer.
what I need is to connect the hmi with my pc to extract the program it contains and save a copy.
I already connect rs232 female cable to pc and I can't communicate.
Does the rs232 cable have configuration?
Hi,
Yes , you can try 2,3,5 to 2,3,5 pin connection or 2,3,5 to 3,2,5.
And which windows operation system are you using ? Where are you from.
Good Luck.
Hello, thanks for the answer.
I'm using windows xp, I'm from Monterrey.
I already provide configuration 2,3 and 5 in rs232 of hmi and 2,3, and 5 with bridges in 7 and 8, 1,4, y6. I found a pdf file this configuration corresponds to a CABS5 communication cable. I successfully made the backup in the hmi version 6.04
in lower versions I cannot communicate by error in the version. is there even a lower version for these hmi? I currently use e-desinger version 7.52 Build 344
thanks and regards
disculpa monterrey , mexico krunal_shah
saludos
Good , please mention your location in profile so this will find by some more people who required support and get trust on this site.
Yes , there was version 6.13 but very old.